Is there any problem with the beam bearing support?
by ken » Tue Aug 29, 2006 11:18 pm
**Is there any problem with the beam bearing support?
-
Senior Member
Check Bearing and Connection
by ken » Tue Aug 29, 2006 11:37 pm
The horizontal beam is supported by the lag-screws from single one-sided plate only. Unless the beam is not carrying the roof bearing load, the beam-end shear and rotation should be checked prior to the design of its supporting connection.
-
Senior Member
by Bruce Pooley » Sun Sep 03, 2006 3:04 pm
Any load on the side beam?
If so, this is a bad detail. It already looks like it has a split forming (horizontal from the lag screw).
-
Senior Member
by ken » Tue Sep 05, 2006 2:55 pm
The load is, not too much, applied at the side member (110 plf) spanning 12 ft.
However, this does not eliminate the connection design requirements.
The contractor changed the original connector design and this was the end results.